Nuclear safety rules may changeIf cables fail, workers race to burning areas
Matthew L. Wald, New York Times
Saturday, November 29, 2003
``...
Washington -- After 10 years of struggling to make reactor owners modify their plants to protect electrical cables from fire, the Nuclear Regulatory Commission is now proposing to amend its own rules, retroactively legalizing an alternate strategy used by many plants but never formally approved.
The change involves the cables that connect the control room with pumps, valves and other equipment needed to shut down a plant safely. Previously, the commission wanted the reactors to separate the control cables for redundant equipment, or install fire detection and suppression equipment or fire barriers, so a single fire could not disable all the cables. It now proposes to accept letting the plants designate technicians who would run through the plant and operate equipment by hand if the control cables had burned away.
...
The reason for the proposal, said Sunil Weerakkody, the section chief for fire protection and special studies, is that over the years the commission's inspectors in the field had informally approved such plans or that reactor owners had made such arrangements without asking permission. According to commission documents, some reactor owners simply asserted that they could use such alternate means under the terms of their licenses.
The commission's lawyers recently concluded that these approvals were not legal. The commission could require an application in each case and then evaluate each one, Weerakkody said, but it lacks the resources to do so and still keep up with its other work.
...
Gunter, in a telephone interview, said that relying on manual actions would mean that plant workers would be counted on to perform heroic, or even suicidal, tasks.
...''