When you say "exceeding our rated thermal power" what are you talking about? (I know but I'd like you to explain so we don't have a bunch of nitpicking)
OK, every power reactor in the United States is licensed for a specific maximum thermal power output, in megawatts thermal. This thermal power is monitored continuously using a calorimetric that measures feedwater flow and temperature to determine the thermal power of the reactor. The instruments that measure these parameters are calibrated to an accuracy +/- 2.5% of full instrument scale. The reactor power level is kept at a level the takes into consideration these measurement uncertainties, and therefore it is assumed that the calorimetric is under-reporting power by 2.75% (2.5 plus 10% uncertainty margin) The reactor is operated at a power level, such that if the instruments are wrong, the reactor thermal power level does not exceed the level allowed by your license. There are usually 8 to 16 flow measurement devices, and 12 to 24 temperature measurement devices inputting to this calculation. They are rules checked against each other automatically, and points that are more than 1% away from there companion points are flagged for calibration checks. This mechanism is controlled by 10-CFR-50 Appendix K.
This is for power operation purposes, there is also the Reactor Protection System which monitors reactor power based on an entirely separate set of instrumentation, and automatically shuts down the reactor if the safety limits are approached. The absolute ceiling for reactor power (both thermal and nuclear power, which ever is greater) as measured by the reactor protection system is set at 103% of the rated licensed thermal or nuclear power. yes, we actually measure neutron flux as an index to nuclear using neutron detectors (inside and outside the core).
Would you relate that to the rated output of the generators, which is the relevant metric for what I was talking about in the discussion on capacity factor?
The steam turbines are slaves to the carnot cycle, as such the maximum mechanical power they can extract from the steam supply system is about 33.67 of the available thermal power, and there is no way the change that. So a 2700 Megawatt Thermal Reactor Plant produces around 909 Megawatt Electric of gross Generation, and about around 870 megawatts of net generation, which is what is available to the grid. The remaining 39 megawatts is used to power the house loads inside the plant. This gross generation number is compared to the thermal generation number, to verify plant efficiency, as a drop in this number indicates wasted energy going somewhere. Any attempt to generate more power that that, will cause a rise in thermal reactor power.
How large is the margin left by the thermal output required to achieve the rating for maximum output of the generators and the maximum thermal output of the reactors?
The margin left before the licensed thermal power limit is exceeded around 2.75% of measure thermal power, or the measurement uncertainty + 10% of the measurement uncertainty.
Was routinely operating within that margin part of the ORIGINAL evaluation of the system?
Yes, the plants were designed to operated at 100% of rated power as base load from the start. Now several, but not nearly all, plants have received power up rates since construction.
In your opinion is the regulatory process for approving changes of this nature weighted in favor of the economic benefits, or the safety considerations?
There have been two methods used to increase the electrical output of units, one is the Appendix K up rate and the other is stretch power up rates.
Appendix K up rates take advantage of the major improvements that have occurred in the ability to measure flow over the past 40 years. This allows the measurement uncertainty of the feedwater flow measurements to be reduced by about 50%. reducing the error margin and allowing plants to run closer to their rated thermal power. Instead of running 2.75% away from the limit, they can run about 1.5% away from the limit, due the the increased accuracy of the instruments.
Stretch Power up rates are a whole different animal, and make use of reanalysis of the primary plant and protective features to increase reactor power 5 to 10%. I am deeply skeptical of stretch power up rates as being weighed too heavily on the economic side. That being said, these uprated plants are still operating within their revised license limits
My unit has not done either of these power up rates, as our main generator cannot produce the additional megawatts electric to perform a stretch power up rate, and Appendix K up rate is still in the planning stage, but at least 3 years away.
|